Negative Tension on Conveyor During Emergency Stop

Posted in: , on 6. May. 2016 - 13:07

One of our clients has a 2.5 km 3500 TPH capacity Belt conveyor. The conveyor is provided with 2 numbers of 1000 KW VFD motors at head end. The conveyor runs smoothly during startup. When there is power failure, the conveyor stops and instantaneously the belt near the tail end on the return side loosens and sags about 600 mm between return rollers and after 30 seconds or so, it takes the normal shape. I am looking for an appropriate solution as we cannot provide flywheel at the drive as the next conveyor is a very short length conveyor and has very less coasting time.

Re: Negative Tension On Conveyor During Emergency Stop

Posted on 7. May. 2016 - 09:21

Apparently an assessment is required.

Based on the information available, in principle, options may include:

1. Manage both the: 2.5 km, and short; conveyors' stopping duration;

Perhaps this is not an option, and/or additional hazard controls [e.g. guards etc] are required.

Although not my preference, subject to the frequency of the event etc, perhaps a "by pass" chute is an option.

2. Manage the "slack side" tension [additional tension, and/or lock in previous average tension],

3. Perhaps a return side brake,

4. Locally reduce the idler spacing.

Regards,

Lyle

Re: Negative Tension On Conveyor During Emergency Stop

Posted on 10. May. 2016 - 10:08
Quote Originally Posted by Lyle BrownView Post
Apparently an assessment is required.

Based on the information available, in principle, options may include:

1. Manage both the: 2.5 km, and short; conveyors' stopping duration;

Perhaps this is not an option, and/or additional hazard controls [e.g. guards etc] are required.

Although not my preference, subject to the frequency of the event etc, perhaps a "by pass" chute is an option.

2. Manage the "slack side" tension [additional tension, and/or lock in previous average tension],

3. Perhaps a return side brake,

4. Locally reduce the idler spacing.

Regards,

Lyle



Thanks for the reply, Mr. Lyle.

My observations are as follows:

The problem arises when conveyor is running at full speed and pull cord switch is pulled. Now we have the following options:

1. Should we increase the counter weight at take-up?

2. We can provide controlled stopping of the conveyor by VFD even if pull cord is pulled.

3. Currently Return idler spacing is 4 meters where 600 mm sag is observed near the tail end area, we can reduce spacing to 2 meters but however we are afraid that by reducing the idler spacing, the extra belt shall approach beyond tail pulley.

What do you think about the above options? Is there any other better solution available.

Another Ten Bobs' Worth.

Posted on 10. May. 2016 - 11:12
Quote Originally Posted by VISHWAJITView Post
Thanks for the reply, Mr. Lyle.

My observations are as follows:

The problem arises when conveyor is running at full speed and pull cord switch is pulled. Now we have the following options:

1. Should we increase the counter weight at take-up? Maybe. Where is the take up?

2. We can provide controlled stopping of the conveyor by VFD even if pull cord is pulled. Not if, as originally stated, there is a power failure.

3. Currently Return idler spacing is 4 meters where 600 mm sag is observed near the tail end area, we can reduce spacing to 2 meters but however we are afraid that by reducing the idler spacing, the extra belt shall approach beyond tail pulley. It seems that any solution is going to be expensive. What is happening to the loaded carrying strand at the tail end? Reducing the idler spacing will only reduce the sag depth: it won't shorten the belt.

What do you think about the above options? Is there any other better solution available.

A sketch will tell a kiloword.

John Gateley johngateley@hotmail.com www.the-credible-bulk.com

High Belt Sag During Stopping At Tail Station - Incline Belt

Posted on 25. May. 2016 - 08:31

We have seen this many times. Bad design. Engineer did not know how to evaluate shock wave dynamics.

Try # 4: One that is a less costly solution. Use a take-up capstan. Best if you do engineering sums to find the best capstan parameters. It has been done many times world wide. There are multiple capstan designs which depends on the TUP design.

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450

Negative Tensions In Belt???

Posted on 25. May. 2016 - 08:35

You cannot have negative tensions in the belt unless the belt is dragging on the ground in the reverse direction to normal belt travel.

You must think through the physics to conclude belt tensions. No such thing as negative tension.

Lawrence Nordell Conveyor Dynamics, Inc. website, email & phone contacts: www.conveyor-dynamics.com nordell@conveyor-dynamics.com phone: USA 360-671-2200 fax: USA 360-671-8450
Roland Heilmann
(not verified)

How Often?

Posted on 26. May. 2016 - 07:57

Dear Mr. VISHWAJIT

Imo these

quote "When there is power failure" and "The problem arises when conveyor is running at full speed and pull cord switch is pulled." unquote

are not regular operational states of your installation. So the technical countermeasure should be adequate to the importance, occurence and danger / potential hazard. First step should be however to prevent above causes as the wording you use seems to indicate a frequency above the usual.

You did not mention the drive equipment, so assuming VFD motors with additional mechanical brakes, there's at least two options:

a) quote "We can provide controlled stopping of the conveyor by VFD" unquote --> Check with your local H&S regulations and / or primary plant specifications if there's a time limit to stopping in emergency cases, and then have the settings of the VFD ramp down set accordingly for the pullcord switch event.

b) for a power grid failure you ought to have mechanical brakes --> here you even could control the brake torque applied by a ramp if using a controlled brake setup with UPS.

Now in the end I'd like to require you to give some reputed and experienced mech. applications / bulk handling engineering company a job as there should be FIRST AND FOREMOST done a thorough analysis of that system, we here can only provide rough ideas which you cannot / should not present as "the solution" (billable).

Regards

R.

Belt Belt Belt Etc.

Posted on 26. May. 2016 - 04:31
Quote Originally Posted by VISHWAJITView Post
One of our clients has a 2.5 km 3500 TPH capacity Belt conveyor. The conveyor is provided with 2 numbers of 1000 KW VFD motors at head end. The conveyor runs smoothly during startup. When there is power failure, the conveyor stops and instantaneously the belt near the tail end on the return side loosens and sags about 600 mm between return rollers and after 30 seconds or so, it takes the normal shape. I am looking for an appropriate solution as we cannot provide flywheel at the drive as the next conveyor is a very short length conveyor and has very less coasting time.

==================================================================================================== ===========

Help us to help us help you;

Has anything changed recently or has there been any maintenance done on this flight of belt??

More than a few issues need to be examined;

Is the upper belt sagging when stopped with a fully loaded belt??

what is your troughing idler distance between idlers?

Is the conveyor flight completely horizontal(zero degrees) or is there a slight slope?

Is this system a steel or cable supported conveyor?

What is the spacing for the troughing idlers and return idlers?

What is the Idler diameter for the troughing and return idlers?

Are fluid drive couplers used or are rubber couplers used for electric motor to reduction gear

to final drive?

1

-----------------------------------------------------------------------------------------------------------------------------------------------------------------------------

Some sag and some slippage can occur on a horizontal flight of belt.

The idlers will roll somewhat unless a head pulley brake is used.

It may be more than likely that a section of belt may need to be cut out and the belt spliced again to remove the sag.

As Mr. Nordell has stated the installation of more idlers is the least costly solution for now until a complete examination of the system by a

qualified person such as Mr. Nordell will find the issues and offer properly engineered and vetted solutions.

2

-----------------------------------------------------------------------------------------------------------------------------------------------------------------------------

Thanks Everybody For The Valuable Inputs

Posted on 3. Jun. 2016 - 01:50

Thanks everybody for the valuable inputs!

In fact, client refused to allow flywheel due to safety reasons as drive is located at 30m floor-elevation.

Conveyor take-up is vertical gravity type and is located near head-end. We held the take-up weight while conveyor was running and gave the conveyor an emergency stop. There was no sag observed at the tail-end now. Which implies that the problem can be sorted out by providing capstan. Since the take-up is vertical gravity type and counter-weight is directly mounted below take-up pulley, there is no take-up rope. Is there any way we can provide capstan in such a scenario?

Although we have temporarily sorted out the problem by providing additional counter-weight, we are looking for a more reliable solution.

Hope to hear more from you guys soon!

Thanks a lot!

Re: Negative Tension On Conveyor During Emergency Stop

Posted on 4. Jun. 2016 - 10:07

Various options exist to restrict a vertical take up's movement, however given the mentioned test method is apparently not in accordance with any accepted practice that I am aware of, I am going to resist specifying it.

Please for the safety of: yourself, and others; consider obtaining suitable professional advice.

Regards,

Lyle

Roland Heilmann
(not verified)

Sure Of What?

Posted on 6. Jun. 2016 - 07:43

Dear Mr. VISHWAJIT,

by not allowing the belt to "draw" the necessary tightening of the upper belt flight out of the gravity take-up you basically drive your conveyor like a fixed-take-up configuration. I very much doubt it has been designed for such procedure and you will overload belt and conveyor equipment beyond the values they were designed for.

You already got a very good worth of, at least, advice, but your conclusion read action astonishes, if not baffles. Is your courage backed up by sound calculation?

Mr. Brown gave you the right direction for the next step to take, are you inclined to follow this good & correct advice?

Regards

R.

Well, Yes But??

Posted on 7. Jun. 2016 - 09:20

Yet again we are fed the question in stages as perpetual 'yes but' style.

I can only reiterate my earlier offering in a changed tense: a picture could have told a kiloword, and leave it there because in these situations the painting specification or cabling layout might be expected to interfere further down the line.