Blower Parellel

Posted in: , on 20. Jan. 2019 - 21:39

Hi

hope to any expert can answer this problem

I design fume extraction system for reclaim rubbe rplant , these is rubber milling area , this area have 10 rubber mills and two horizontal strainers. I used two centrifugal blowers (40000 CFm X 16 inwg ) for extarction . all canopy hoods , selection complience with ASHARE standards.

my problem is fan delivery connected to same chimeney, out let is parallel , but in let I was not common , system have separate extaction lines.

so using blower in parallel , I have to common inlet ductings ?

or outlet common is enough ?

please advice us

regards

uditha

uditha

Re: Blower Parellel

Posted on 21. Jan. 2019 - 11:17

Dear uditha

Whether the outlets of the 2 fans should be in parallel is not a real issue.

Whether the fans have their own outlet into the atmosphere or into a common chimney, the outlet pressure of the 2 parallel fans is equal.

If the intakes are extracting gas from different sources, that is a different case.

If the 2 supposed, extraction pipes have different resistance, the extraction lines must be kept separate.

It is all a matter of calculating the required gas flows and pressure drops in the pipelines and check those against the centrifugal fan curves (parallel or single)

The arrangement depends on what is required from the installation.

Teus

Re: Blower Parellel

Posted on 21. Jan. 2019 - 07:38
Quote Originally Posted by Teus TuinenburgView Post
Dear uditha

Whether the outlets of the 2 fans should be in parallel is not a real issue.

Whether the fans have their own outlet into the atmosphere or into a common chimney, the outlet pressure of the 2 parallel fans is equal.

If the intakes are extracting gas from different sources, that is a different case.

If the 2 supposed, extraction pipes have different resistance, the extraction lines must be kept separate.

It is all a matter of calculating the required gas flows and pressure drops in the pipelines and check those against the centrifugal fan curves (parallel or single)

The arrangement depends on what is required from the installation.

Dear Mr. Tesus

thanks for comment , I attched my arrangement drawing , outlet is common chimney , but inlet not

fume4#bulk#forum

common arrangement , but parallel blowers Input as well as output should have to common ?

Regrads

uditha

uditha

Re: Blower Parellel

Posted on 22. Jan. 2019 - 08:35

Dear uditha

In your drawing, the 2 fan outlets can discharge in a shared chimney.

The chimney diameter must have a diameter, which is designed for the combined flow.

If the intakes are extracting gas from different sources and have different pipe resistances. The extraction lines must be kept separate.

Calculate the required gas flows and pressure drops in the pipelines and branches and check those against the centrifugal fan curves.

Then you know, if the installation meets the requirements.

If all the gas sources are operating simultaneously, this might be not that easy.

Teus

Re: Blower Parellel

Posted on 22. Jan. 2019 - 05:53

Dear Mr. Tesus ,

thanks for vital information , calculated flow rate for each side 40000CFM , and static pressure 12 inWG - side A , 40,000 CFM X14 inWG side B , there for we ordered two blowers 40,000 CFM X 16inWG

side A and B have separate suction lines , which are not common

But discharge line is common

I see some books , Blower inlet lines must have to common (near suction end , common duct line (blower A , and B) is this essential ?

system pressure cannot equal both sides (difficult , but can)

this is not issue for chiminey back pressure ?

regards

uditha

uditha

Re: Blower Parellel

Posted on 22. Jan. 2019 - 07:14

Dear uditha

Actually, you have designed 2 separate systems with a centrifugal system for each system.

The only thing is that the 2 fans discharge into a common chimney.

For both fan outlets, the discharge pressure is determined by the chimney flow resistance.

The chimney design must be for both fans running, whereby only a minor, negligible pressure drop is generated.

The performance of the whole systems must be checked by calculation, using the pressure/flow curves of the 2 fans. A Variable Frequency Drive can help to create the required conditions and performance.


I see some books, Blower inlet lines must have to common (near suction end, common duct line (blower A, and B) is this essential?

There is no MUST.

Teus