Re: Measuring Veloctiy In Duct
Dear Niaz,
Make your own Pitot-tube from 4/6 mm dia pipe and transparant plastic tubing.
The length of the pitot tube can be chosen in relation to the duct you want to measure.
You need to drill ome small holes in the duct. These holes can be closed later on.
see the attache file.
success
teus
Attachments
■
Teus
Re: Measuring Veloctiy In Duct
Nice simple design! ■
Re: Measuring Veloctiy In Duct
Dear Teus,
Thank you for your advice. But is there any limitation for doing this test, eg. the length of staright duct without any bends?
and do you have any solution for measuring the capture velocity near the hood?
Regards
Niaz ■
Re: Measuring Veloctiy In Duct
Dear Niaz,
Where you keep the Pitot-tube measuring point, you will measure the velocity as a vector in the direction of the tube.
(Also near the hood)
How meaningfull the location is, where you measure, is more or less up to your own judgement.
By measuring at various places in a cross section or space, you can reconstruct a velocity profile and decide whether that measurement gives you the information that you wanted.
By disconnecting one of the two sides of the U-tube, you can measure the static pressure or the static + velocity pressure.
(providing that the internal pressure does not empty your U-tube)
success
teus ■
Teus
Re: Measuring Veloctiy In Duct
hi there
when measuring the ducting with dust laden air, if you use L type pitot and S type pitot using manometer.
why the pressure reading of L type pitot is higher if compare to S type by 4-6 times?
any explaination for this..........
tq ■
Measuring Velocity In Duct
Mall
An S type pitot needs to be calibrated against a standard (L type) and a correction factor applied. The factor will be something like 0.80 or 0.85, depending.
Also, velocity pressure is typically a very low number and you will have difficulty measuring it accurately with the vertical plastic tube manometer. Use an inclined manometer (expanded scale) or Magnehelic gauge or digital manometer.
Michael Reid. ■
Re: Measuring Veloctiy In Duct
hi
tq
the factor is 0.84 for s type pitot and i use digital manometer attach with pitot tube.
due to high dust laden air so i keep putting in and out my pitot tube. i only take into account the reading if the pitot tube is not plugging.
so take quite long time to do traverse.......... ■
Measuring Velocity In Duct
Mall,
Yes, heavy dust load sometimes means you have to remove the pitot after each measurement and blow out the dust. Takes time.
How easy is it to read your digital manometer? If it has an averaging function, you will get good accuracy and quick readings. If not, you have to guess which of the fast-changing jumble of numbers is the correct reading. Accuracy will suffer.
Michael Reid. ■
Re: Measuring Veloctiy In Duct
mike
is there any different in term of pressure reading using L type and S type pitot becoz S type internal diameter of the tube is larger than L type.
for your info i use dwyer digital manometer model 477
regards ■
Re: Measuring Veloctiy In Duct
Mall,
The S type and L pitot should give the same reading, allowing for the correction to be applied to the S type. Tube diameter does not matter.
I do not know the Dwyer 477 but my experience with other Dwyer digital manometers is that they are impossible to use because of the constant fluctuation of the digital readout. Any reading you accept has to be a guess. Much better to use one of their Magnehelic analogue gauges.
My own instrument is an Alnor AXD Mod. 560M which allows you to average the pressure readings over a set period, say 10 sec. (It also calculates flow if you give it temp., duct size and B.P. It compensates for static pressure).
Send me a sketch of your duct/fan layout and I will try to suggest more.
Michael Reid. ■
Re: Measuring Veloctiy In Duct
hi there
is there any method to estimate dust load in the dust laden air suck by bag filter in the ducting
tq ■
Measuring Velocity In Duct
Mall,
There is a method called isokinetic sampling. It uses a sampling train consisting of a vacuum pump, sampling nozzles, probe and filters to extract a sample of gas and separate out the dust. There is also a condenser to separate the moisture of combustion.
It requires special equipment and training and is usually done by specialist contractors who do emission monitoring. Various National Standards describe the method.
Michael Reid. ■
Re: Measuring Veloctiy In Duct
tq
but the equipment is so expensive.
do you have any more simple method to estimate the dust load without high investment for the equipment?
tq ■
Measuring Velocity In Duct.
Mall,
Maybe you could play around with a vacuum cleaner for a rough estimate otherwise, the easiest and cheapest way is to get a specialist to do the job for you. One off cost with no investment in equipment.
Michael Reid. ■
Dust Load Measuring
mall,
please find the attached file as the Emtronc for measuring dust load of Mikropul.de
Attachments
■
Measuring Dust Load
This device still needs to be calibrated with a proper sampling test.
Michael Reid. ■
Measuring veloctiy in duct
Dears,
We have a suction point at the bottom of a chute from iron ore hopper to conveyor in a crushing plant. the height of chute is about 7m. the dust from the falling of particles is so high that the hood doesn't have appropriate suction, even by changing the damper positions and increasing the flow at that point.
Would you please inform us how can we measure the capture velocity at the inlet of hood or velocity in the duct and what are the proper conditions for measuring the real velocity?
Do you have any solutions for lowering the dust?
Thanks
Niaz ■